5/16/2012 12:36 AM | |
Posts: 14 Rating:
|
Thanks, the @GLOB is configed, and the adress at its connector is not xxx.X01. The CTV have error 6056. All the CPUs have send and receive telegram,so thetotal number of telegrams are 20, and the total number of bytes is 2100. Now the CP51M1 is installed in 19 slot. I have check the channel names several times, all names are unique. Firstly all the communications are ok, and only the communication CPU5 sends to CPU4 interrupt after 5 days, is there something wrong in communication buffer or CPU5, or maybe the communication buffer overflow after 5 days. AttachmentTDC Communication Problem.pdf (578 Downloads) |
5/16/2012 5:29 AM | |
Joined: 8/25/2006 Last visit: 9/16/2025 Posts: 2218 Rating:
|
Hello. What version of D7-SYS you are using? If it is V7.0 or higher look at the followingrestrictionsof using CP51M1 and CP50M1. But at first I recommend to insert CP51M1 into free slot 3 of your rack and reconfigure all HW addresses of CPU-CPU couplings, of course if if you have no above mentioned restrictions. This is the old rule from Simadyn D, that communication buffer must be between 1 and 2 CPU.
|
5/16/2012 9:35 AM | |
Posts: 14 Rating:
|
1. The D7-SYS version using is V7.1. 2. For the restriction problem, The required min. hardware release for the CP50M1 module (order no. 6DD1661-0AD1) is 2, now the module inuse is 2, and the firmware of the module is V1.1.3. AttachmentTDC Communication Problem 20120516.pdf (489 Downloads) |
5/16/2012 10:37 AM | |
Joined: 8/25/2006 Last visit: 9/16/2025 Posts: 2218 Rating:
|
Hello. I don't see any other problems with your configuration. Next step will be aSupport request.
Anyway, if you have spare CPU, try to replace your CPU no.5 with new one and look how it will work. |
Last edited by: KSN at: 5/16/2012 1:08 PM |
|
Follow us on