5/3/2024 2:56 PM | |
Joined: 7/7/2010 Last visit: 5/17/2024 Posts: 14751 Rating: (2374)
What is the exact part # and what is the hardware revision (1.x or 2.x?) Is this firmware compatible with your hardware: https://support.industry.siemens.com/cs/document/109775640
science guy |
5/3/2024 4:46 PM | |
Joined: 4/12/2024 Last visit: 5/3/2024 Posts: 2 Rating: (0) |
Q: What is the exact part # and what is the hardware revision (1.x or 2.x?) A: The article number of the module I am using is: 6GK7 242-7KX31-0XE0 (hardware version 1). Q: Is this firmware compatible with your hardware:https://support.industry.siemens.com/cs/document/109775640? A: It is not compatible, because the hardware version is 1.x and I am using TIA Portal version 13 sp2. |
5/3/2024 5:20 PM | |
I think the problem is that you are using Portal V13 SP2. Upgrade the project to V15.1 or higher and you should be able to use FW 3.1.x According to the delivery release for the provided Siemens part #, it has Hardware rev 2. If you inspect the module and look at the higher density labeling (sometimes on the side of the module), you can see the HW rev, like HW: 1.0 or HW: 2.0. What does your module have? Apparently, there is no firmware for the v2 (which is supposedly the hardware rev as part of the common name). If you must use V13 SP2, you may not be able to use that module. Suggest submitting a Siemens Support Request (via the gray bar link "Support Request" above these online forums.