12/12/2008 9:09 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating:
Hello, To the meaning of SIL levels: ====================== SILs are defined in the IEC61508 standard for functional safety in electrical electronic/programmable electronic safety-related systems. The basic idea of the measures taken to guaranty the functional safety is to detect as far as possible dangerous failures (= failures that put the safety in question) even before they have a negative impact on the safety. To evaluate how far this purpose is reached, statistical values (probability)are used that express the residual risk of having a dangerous failure.The SIL value can range from 1 (the lowest integrity) to 4 (the highest integrity). Further more, the safety system is separated into two modes of operation: low demand mode of operation, which gives a probability of failure to perform the designed function on demand, and high demand, or continuous, mode of operation which measures the probability of failure per hour. In the evaluation of a safety function, not only the involved PLC is considered, but also the sensors and the actuators used. To Simatic Safety Systems ===================== It would be to long to list here all the specifics of Simatic failsafe PLCs. Have a look to the following manual that in chapter 1 gives an overview of failsafe systems, in chapter 2 configurations and help for selection, .... http://support.automation.siemens.com/WW/view/en/12490443 |