2/17/2025 11:10 AM | |
Joined: 7/11/2024 Last visit: 8/4/2025 Posts: 200 Rating:
|
Hi cfllex_tech49 I don't really understand all of your questions, maybe you should try to write them in a more organized way... If you want to retrieve a program from an S7 PLC, you can use TIA Portal. You can connect online to the PLC and select the option ‘upload device as a new station’. This will upload the entire project, including the hardware configuration and the program, from the PLC to your computer. Once the upload is complete, save the project on your computer. Another option is to create the backup on a SIMATIC memory card. Take a look at: Backup and restore options Good luck!! |
If this post has been useful, don't forget to rate it!😊 |
|
2/18/2025 6:16 AM | |
Joined: 2/10/2025 Last visit: 9/4/2025 Posts: 25 Rating:
|
the Step 7 Plc program was written with simatic manager, The first thing I'm trying to do is verify the offline program i have saved is the most recent copy of the plc program and hardware profile, How would I do this? |
2/21/2025 6:41 PM | |
Joined: 9/21/2012 Last visit: 9/4/2025 Posts: 4703 Rating:
|
Make sure you have a working online connection to the PLC. Then make sure you are offline and in the program blocks folder, select compare with online. Then Simatic Manager will perform a comparsion between the online and offline program. |
2/22/2025 8:18 PM | |
Joined: 2/10/2025 Last visit: 9/4/2025 Posts: 25 Rating:
|
will this also compare the hardware configuration? |