Hello. What is the value of P082, when F005 occurs? Check also connections of field supply (AC and DC side).
|
4/29/2013 2:53 PM | |
Joined: 8/25/2006 Last visit: 10/18/2024 Posts: 2209 Rating: (279) |
Hello. Previously you have wrote:
Please specify the complete order number of the drive. Have you followed step-by-step start-up procedure described in themanual(section 7.5), especially did you reduce rated converter armature and field currents (page 7/19), as you try to work on a 65A motor with 850A converter.
|
4/29/2013 3:49 PM | |
Posts: 14 Rating: (0) |
Dear sir thank you for your reply i am working on drive, type:D520/850 Merg -GeGE4V62-4A 6RA 2487-4GV62-0 with regards Vikas Prakash singh |