Hello; The Modbus TCP license you are pointing to is for S7-300 CPUs with an integrated Profinet port, which corresponds to the S7-317-2PN/DP you will be working with. You can use this license for TIA Portal Professional and for Simatic manager (step 7 v5.x), as you can see in the following link: - How do you establish a Modbus/TCP communication from a SIMATIC S7-300/S7-400 and where can you find further information? https://support.industry.siemens.com/cs/ww/en/view/22660304 Links from this document:
Modbus/TCP PN CPU(Article number: 6AV6676-6MB20-3AX0) Download:109745187¸ The demo version can run without license, for testing purposes. If the CPU cannot detect the license installation, the diagnostic LEDs of the CPU will remain active and the diagnostic buffer will continuously log fault messages until the license is installed, This will not impede functionnalities of the driver. but it will be a constant annoyance... Also:
This documentation should give you most of what you need to know about setting up the Modbus TCP sriver (client or server) on the CPU 317-2PN/DP. Hope this helps, Daniel Chartier |