11/5/2014 5:51 PM | |
Joined: 7/8/2014 Last visit: 2/21/2023 Posts: 12 Rating: (0) |
I think that you are again right. It looks like most of the data are DINI and need to be divided by 100. Little bit strange format for me because I expected REAL. I will check for error code tomorrow when I will do additional tests. Regards Lukasz
AttachmentDirisA40ModbusTcp.pdf (438 Downloads) |
11/6/2014 11:37 AM | |
Joined: 7/8/2014 Last visit: 2/21/2023 Posts: 12 Rating: (0) |
I check and error is from function AG_SEN. I also run Special Diagnostic for card CP343-1 and there when I monitor status of connection once is closed and after 1 or 2 s established and again closed. It looks like one site (CP343-1 or Diris) close the connection. Now the question how to know where exactly is the problem ? AttachmentOnlineData.zip (388 Downloads) |
11/10/2014 1:26 PM | |
Joined: 10/21/2011 Last visit: 7/15/2021 Posts: 57 Rating: (17) |
Perhaps in a wireshark trace you could see why the connection gets shut down. |
11/11/2014 2:38 PM | |
Joined: 7/8/2014 Last visit: 2/21/2023 Posts: 12 Rating: (0) |
Hi Gwawl, I already try to look on wireshark trace and for me it looks like Diris (IP 172.16.32.227) from time to time not responding on request send from CP343-1 (IP 172.16.32.227) . I already try to increasy MONITOR time in FB108 block even to 20 s but it is still the same. Mayby next week I will have time to connect PLC to diffrent place in the network. I will let you know when I will find root cause of the problem. Regards Lukasz AttachmentCapturedData.zip (339 Downloads) |