How to change the block version? Thanks |
10/16/2020 8:54 AM | |
Joined: 10/3/2008 Last visit: 8/28/2024 Posts: 961 Rating: (124)
|
For writing you must only change the runtime parameter WRITE_READ to TRUE. Change also the runtime parameters START_ADDRESS and LENGTH and set ENQ_ENR to TRUE. You don't need an additional modbus block instance for writing. You can use 1 modbus block for reading and writing to the same communication partner. In the parameter datablock you parameterize in which datablock the modbus register should be mapped. |