8/23/2019 2:28 PM | |
Joined: 12/6/2016 Last visit: 6/12/2023 Posts: 57 Rating: (0) |
welcome everybody In this example (ahmad.zip) there is the following Input I0.0 gives pulses to C0 If the number of pulses is 5 Output Q0.0 will be activated After a certain time it is entered from VW10 If the number of pulses in C0 does not reach 10, Q0.0 will stop working, but if the number becomes 10 or more will follow the work of Q0.0 Now I want you to help: I want to reset the value of the counter C0 every (1 minute) without stopping the output of Q0.0 In addition to displaying the value of the counter C0 on the memory VD100 to be used in the HMI, but this paragraph has a condition which is: The first minute the number of pulses of the counter is 10, this number will be displayed on the HMI and the counter will be reset The second minute, for example, the number of pulses of the counter 15 will be displayed number 15 on the HMI instead of the number 10 and reset the counter every minute and maintain the output Q0.0 working condition as mentioned earlier Attachmentahmad.zip (240 Downloads) |
Last edited by: Jen_Moderator at: 08/26/2019 08:33:25Edited text for better reading. Al-Nassim Company |
8/25/2019 12:11 PM | |
Accessed to resolve the problem thank you