Hi, is it possible to install a logo hardware on two racks? I have no enough space for all the modules and i need to install it on two racks (as S7 PLC). Thanks |
| 10/20/2022 8:14 AM | |
|
Joined: 5/30/2022 Last visit: 12/17/2025 Posts: 634 Rating:
|
Hi AutoGen_3394064, The LOGO! modules must be connected to the CPU, so installation in 2 racks is not possible. You would need to use 2 LOGO!, one slave of the other, I attach information about it: Changing LOGO! to master/slave mode |
|