(0)| 4/26/2023 12:12 PM | |
|
Joined: 10/11/2006 Last visit: 12/22/2025 Posts: 6062 Rating:
|
Hello, the equipment manual for Booksize power units shows in chapter 4.9 the possible combinations of line modules with filters and reactors. Smart Line Modules Booksize can be used without line filter if no radio interference suppression is required. AttachmentCombination options Smart Line Modules with line filters and line reactors.png (567 Downloads) |
|
With best regards, |
|
| 4/28/2023 12:31 AM | |
|
Joined: 10/17/2007 Last visit: 12/23/2025 Posts: 4566 Rating:
|
Thanks for your answer--I read Ch. 4.9 , not sure if ALM 80KW and 120KW can be used with reactor only without Active Interface Module, I have NC62 (2016 version) --I attach page of smart line module select reactor , please suggest newer version of NC62 actually I have customer who is repair and spare parts company, they only wnat to test purpose to power up ALM module 80 KW and 120KW , not running long time --please suggest if it is possible
|
|
If you like my comments please |
|
| 5/4/2023 6:04 AM | |
|
Joined: 10/11/2006 Last visit: 12/22/2025 Posts: 6062 Rating:
|
Hello, there is also an overview for Active Line Modules. There you can find, that they can be used with HFD line reactors and damping resistor, but the recommended combination for new systems is the one with Active Interface Modules instead of HFD line reactors. That's why the HFD line recators are not any more shown in the catalogue. The actual S120 catalogue is D21.4. |
|
With best regards, |
|
| 5/8/2023 11:26 AM | |
|
Joined: 10/11/2006 Last visit: 12/22/2025 Posts: 6062 Rating:
|
Hello, there is a description in the function manual for S120. AttachmentInfeed control from Drive Function Manual S120 0620 en-US.pdf (521 Downloads) |
|
With best regards, |
|
This contribution was helpful to
|
|