op17 DP continous restart , it connect to S7 300 cpu 313c , please what are the reasons for this? |
| 2/26/2012 4:09 PM | |
|
Posts: 8946 Rating:
|
Restart only if connected to plc? Than check if adress is used twice! |
| 2/26/2012 5:39 PM | |
|
Joined: 3/21/2006 Last visit: 1/10/2026 Posts: 10247 Rating:
|
Hello, How does happen that behavior of OP27DP? Best regards, Hristo Mihalev |
| 3/1/2012 6:24 PM | |
|
Posts: 3 Rating:
|
Thanks for all of you I found that the MPI interface in panel side is damaged , and i migrated it to op177b.
|