(0)| 8/26/2019 12:36 PM | |
|
Posts: 45 Rating:
|
Hi can you tell us what is the communication used between PLC and FM. is it 4 to 20 mA or Profibus ? Seems to be Output scaling Issue. |
| 8/26/2019 3:27 PM | |
|
Joined: 3/28/2010 Last visit: 12/23/2025 Posts: 1201 Rating:
|
What size (diameter) is the flow element in the tube/pipe? |
| 9/4/2019 9:34 AM | |
|
Posts: 93 Rating:
|
Hi, Is this flow continuously fluctuating? If yes, Check the grounding is proper on flow sensor side? Quick check you can do is by connecting a small earthing wire on one of flange bolts. Then connect to instrument earth (Not electrical earth) or just touch to some metal pole which is grounded or just bolt it on ground/floor. Refer to manual for types of grounding you need to consider while installing. Manual can be downloaded from Siemens website: https://support.industry.siemens.com/cs/ww/en/view/45345673 Hope this helps. Regards, Davinder Singh |
Last edited by: Jen_Moderator at: 09/04/2019 11:35:41Optimized link. |
|