(0)| 7/16/2020 9:24 AM | |
|
Posts: 302 Rating:
|
However who have the transister model could test if it can work like KiloHertzs switching or not. |
| 7/20/2020 11:12 AM | |
|
Joined: 12/18/2014 Last visit: 12/24/2025 Posts: 36369 Rating:
|
And the manual says also: The maximum switching rate is only depent on the switching program's cycle time.
AttachmentLOGO! 8 manual 0BA8 2017_11 xxxx8-0BA0 page 326.pdf (499 Downloads) |
| 7/22/2020 11:17 AM | |
|
Joined: 12/18/2014 Last visit: 12/24/2025 Posts: 36369 Rating:
|
In the attachment screenshots of the test with a LOGO! 8.2. - Screenshot of the test program. - Screenshot with simple web server. - Screenshot with extended web server. Without using the simple web server, the cycle frequency is approx. 25 Hz higher than when using the simple web server. The cycle frequencies also fluctuate slightly.
AttachmentScreenshots.zip (455 Downloads) |