3/24/2021 5:03 AM | |
Joined: 12/18/2014 Last visit: 9/2/2025 Posts: 35914 Rating:
|
Are the power supplies for the sensor and the AM2 module the same? |
3/24/2021 5:15 AM | |
Joined: 12/18/2014 Last visit: 9/2/2025 Posts: 35914 Rating:
|
No, the AM2 module does not have to be configured in LSC. The analog amplifier must be set to the sensor type 4-20 mA. The values for Min and Max should be set in the same way as the physical measuring range of the sensor. Take a look at the attachment. There is the start menu of the LOGO! explained. On screen 3/9 you can see the values after the A / D converter of AIs 1-5. 4 mA = 200 and 20 mA = 1000. The green LED says that the module is communicating with the module on the left.
AttachmentLOGO! 8 manual 0BA8 2020_10 xxxx8-0BA1 page 355.pdf (441 Downloads) |
3/24/2021 6:17 AM | |
Joined: 12/18/2014 Last visit: 9/2/2025 Posts: 35914 Rating:
|
That's why I attached page 355 from the manual in my post above. |
Follow us on