3/19/2024 2:48 PM | |
Joined: 3/27/2008 Last visit: 10/28/2024 Posts: 1143 Rating: (142)
|
Attached is a plan for switching the relay DO2 using settings in P2155, also included is adjustments for Hysteresis and delay time which is useful. To get a view if the parameters I have used Siemens 'Drive Monitor', vis a RS 232 / 485 converter, whilst not essential, most but not all of the parameters can be seen and changed on a PC. I do not believe there is a PC base configurator for V20 yet? Also: Micromaster MM440 issue 10/06, this is an old manual, still available for download, but useful for getting a look at the V20 parameters as they are similar, and some of the drawings are better. See how this works, and come back if you have any snags with this. Tractor AttachmentV20 relay output switch at Hz setting.pptx (504 Downloads) |
Last edited by: Tractor at: 03/19/2024 14:53:22Tractor |
|
This contribution was helpful to1 thankful Users |
3/20/2024 9:53 AM | |
Joined: 3/27/2008 Last visit: 10/28/2024 Posts: 1143 Rating: (142)
|
Hi, See attached version, to use CMP function to monitor the analogue input, I have used the relay to monitor the operation. Yes, I find Drive Monitor useful to get into the V20, but as as been pointed out it is not 'supported' as a 'tool' by Siemens. See how this works, come back if I have missed something. Tractor AttachmentV20 relay output switch at Hz setting.pptx (497 Downloads) |
Tractor |
|
3/21/2024 9:33 AM | |
Joined: 3/27/2008 Last visit: 10/28/2024 Posts: 1143 Rating: (142)
|
Thanks for the feedback Tractor |
Tractor |
|