(1)| 7/28/2011 2:05 PM | |
Posts: 16 Rating:
I have need FB41 PID example .how is fb41 use? |
| 7/28/2011 7:47 PM | |
Joined: 1/28/2009 Last visit: 1/5/2026 Posts: 6892 Rating:
Dear kutilati Check the attachment for as an example for FB41 and online manual of the function.The process value is read from IW100 and its range is from 0 to 200.The output of PID controller is written QW100(0 to 27647).Also check the variable table in the S7 program, it makes all necessary control variables available for you. Regards Attachmenthd_FB41_EX.zip (12711 Downloads) |
| 8/5/2011 11:39 AM | |
Joined: 4/24/2008 Last visit: 1/15/2025 Posts: 213 Rating:
look here http://support.automation.siemens.com/WW/view/en/16532187 There is the link for the example for SFB41 you can use it. You only need to change the SFB41 to FB41. |
| 8/5/2011 12:07 PM | |
SIMATIC S7-300 CPU 31xC Technological Functions |
| 8/5/2011 11:39 PM | |
Hi Check the attachment "zEn26_04_TF_____31xC_PID", you can check application of SFB41 in "Controlling 2 CONT_C". Note there is no connection to input or output signals.LMN fed to INV parameter of FB100 process simulator and the result OUTV is transferred as input to PV_IN of SFB41. Regards AttachmentPid_test.zip (7637 Downloads) |
| 8/20/2022 6:36 PM | |
Posts: 11 Rating:
Hi Please check the video for your reference. https://www.youtube.com/watch?v=m4lECEdj_84 |