5/3/2017 9:24 AM | |
Joined: 5/28/2008 Last visit: 9/3/2025 Posts: 4522 Rating:
|
Hello, I have never tried to connect MM4 with that cable. But you can follow instructions in the *.ppt slides attached in the following link: Hope this helps. |
Last edited by: Ayman Elotaify at: 5/3/2017 9:25:03 AMAyman Elotaify |
|
This contribution was helpful to
2 thankful Users |
5/3/2017 6:25 PM | |
Joined: 11/18/2010 Last visit: 5/17/2025 Posts: 14 Rating:
|
Thank you for your help, this instructions is using "connection kit for PC to converter (via BOP link - RS232 port), it is not using PC adapter RS232 to PPI. By the way I solved my problem, I used RS232/PPI cable but we have to supply power for that calbe, wiring should be as bellow: PC Adapter --------- MM440 |
Last edited by: thai_truong at: 5/3/2017 6:32:34 PM |
|
5/3/2017 7:00 PM | |
Joined: 11/18/2010 Last visit: 5/17/2025 Posts: 14 Rating:
|
Hello Ayman Elotaify and Vithani, Another issue, My drive MM440 has problem then I tried to connect PC (STARTER) to drive to find which wrong parameters but still stuck with it. The problem is when I start drive with preset frequency (ex 30Hz) but drive always start with max frequency 130Hz then frequency quickly down to negative value that causes motor run with reverse direction, after a few seconds motor stops and increase speed to preset frequency (30Hz) Attachment is parameters I uploaded from drive using STATER, could you please take a look at it as if you could find any wrong parameters? thank you! Attachmentbackup_drive.zip (1509 Downloads) |
Last edited by: thai_truong at: 5/3/2017 7:02:13 PM |
|
9/27/2021 6:38 PM | |
Posts: 31 Rating:
|
Sir, which conveter you used, bidirectional or single directional? |