10/4/2008 4:21 PM | |
Joined: 9/27/2006 Last visit: 9/14/2025 Posts: 12408 Rating:
|
Hello venugopal; The 6ES7 331-7KF02-0AB0 module is capable of measuring current in boith 2-wire and 4-wire configurations, but the selector module (on the outside of the physical module) must be set to "D" for 2-wire measurements, and to "C" for 4-wire connections. Of course the hardware configuration of the analog module channelmust be done correctly in the HWConfig editor. This is shown in the S7-300 Module Data manual: Measuring range Measuring range module setting 2-wire transducer 4 mA to 20 mA D 4-wire transducer± 3.2 mA C ± 10 mA 0 mA to 20 mA 4 mA to 20 mA ± 20 mA
|
10/7/2008 10:10 AM | |
Posts: 12 Rating:
|
Dear Umar, There is a seperate duct for power cable and control cable. Regards, Venugopal.T |
10/23/2008 1:47 AM | |
Joined: 7/2/2008 Last visit: 8/7/2025 Posts: 928 Rating:
|
You said you measured current from 4-20mA. Attachment7KF02 CMV.pdf (1037 Downloads) |
10/24/2010 9:21 PM | |
Posts: 10 Rating:
|
Your Problem will be surely Solve ! |
This contribution was helpful to
1 thankful Users |