Lol, sorry, probably I did not understand. You really think that a one point nine Nm motor can give 10-11 Nm ?
Maybe, but if you think that it is correct to say that torque reference for a 1.9 Nm is 11-12 Nm then I think that I am not the only one to have an incorrect concept of nominal torque. I have attached the data sheet of your 1.9 Nm. Can you show us where it should give out 10-11 Nm ? Oh please.
Attachment1FL6042-1AF61-2AA1_datasheet_en.pdf (223 Downloads) |
Searching for Siemens used/new equipments ? |
|
3/10/2025 12:23 PM | |
Joined: 9/23/2005 Last visit: 9/12/2025 Posts: 5116 Rating:
|
This is "my" motor - 1FT7036-5AK70-1FH0. Yes, it's rather high end. Actually its nominal S1@100K torque is 1.7 Nm - my bad, I've read its approx nominal torque from the chart at first. Sorry for that. To achieve this level of performance an S120 ALM @ 480V and appropriate MM are required. Anyway, putting aside discussion what is feasible and what's not, please read the fancy manual to understand how p2003 is calculated. Spoiler - it has something to do with max motor current and its torque constant. BTW, nominal torque of a motor you presented is 1.27 Nm. |