Hello Santonit; I am afraid there is no way you can upload a GD table from the PLC program. When you create a GD table, it is not saved in the PLC as a loadable (and retrieval) block such as a DB, FB or FC, but as a SDB, such as hardware configuration or network data. To look at this type of information, Siemens provides special tools, such as HWConfig or Netpro. But they never gave out a tool for GD tables. The following link shows various posts asking very similar questions over the years, unfortunately with very similar answets: https://sieportal.siemens.com/su/blSh1 Hope this helps, Daniel Chartier |