12/3/2016 6:32 PM | |
Joined: 8/25/2006 Last visit: 8/22/2025 Posts: 2218 Rating:
Hello. 6DD1683-0CH0 is a part of hole subrack UR5213. This is the spare part for replacement of power supply with fans. It looks like you have the first version of rack UR5213 with order number 6DD1682-0CH0, now it is compatible with the rack 6DD1682-0CH2. The difference you can find in this file. |
12/6/2016 5:29 AM | |
Joined: 10/13/2014 Last visit: 3/27/2023 Posts: 30 Rating:
Dear Sir, Thank you, Then i can conclude that TDC 6DD1683-0CH0 is compatible with simatic TDC 6DD1682-0CH3 (UR6021) |
12/6/2016 6:28 AM | |
Hello. 6DD1682-0CH0 - Simatic TDC rack UR5213, first version, this is your rack. 6DD1683-0CH0 - power supply with fans PS5213, spare part for the rack UR5213. 6DD1682-0CH2 - Simatic TDC rack UR5213, second version, it is a replacement for first version of UR5213. 6DD1682-0CH3 - Simatic TDC rack UR6021, newest version, replacement for UR5213. You can use UR6021 instead of UR5213, but read the restrictions in the above mentioned file chapter 4.1.1. You can't use new CPU555 with your old modules in UR6021. Also you will need another backup battery for UR6021. |
12/8/2016 12:06 PM | |
Hello. It is written in the above mentioned manual. For UR6021 you need 3.6V 2.3Ah battery 6ES7971-0BA00. |
