4/19/2022 10:09 AM | |
Joined: 10/11/2006 Last visit: 9/15/2025 Posts: 6039 Rating:
|
Dear Aled1197, Normaly the TO does the homing by it self, and the V90 is just a simple closed loop speed controlled axis. No Sinapos is needed. When Sina_Pos is in use, then the absolute encoder has to be adjusted and the drive with its encoder has to be homed. according the manual in Application example: Referring the manual: SIMATIC S7-1500 S7-1500/S7-1500T Axis functions V6.0 as of STEP 7 V17 Section 3.12: In the following cases, the "Homed" status is reset, and the technology object must be rehomed. • Replacement of the CPU • Modification of the encoder configuration • Restoration of the CPU factory settings • Transfer of a different project into the controller When you use a new absolute value encoder you need to home the absolute encoder once again. Resetting the memory of the CPU or upgrading a project does not require another absolute encoder adjustment. Use for encoder connection: Absolute value with setting cyclic absolute
|
With best regards, |
|
10/7/2022 7:18 AM | |
Joined: 9/2/2022 Last visit: 4/3/2024 Posts: 1 Rating:
|
Memory reset from TIA portal really works. Thanks Yu-Wen. Regards Nitin |
5/30/2023 12:27 PM | |
Joined: 10/1/2021 Last visit: 8/9/2025 Posts: 5 Rating:
|
Memory Reset Really Works Thanks |
9/26/2023 12:29 PM | |
Joined: 10/23/2020 Last visit: 9/26/2023 Posts: 1 Rating:
|
MRES really solved , just update. |
12/11/2024 1:03 PM | |
Joined: 12/11/2024 Last visit: 4/29/2025 Posts: 1 Rating:
|
We had same problem MRES solved thank you. |
4/28/2025 4:00 PM | |
Joined: 1/24/2022 Last visit: 8/29/2025 Posts: 2 Rating:
|
Is any data lost if I press mres? |