1/29/2016 7:40 AM | |
Posts: 32 Rating: (1) |
Hi Albis, I am facing some issue regarding BTU meter integration to Xwp..Details are as follow.. 1.Interfacing PXC001.D V5.1 with siemens BTU meter UH50-G82C-EN06-E with WZU-MB G4 module. 2.Data is coming on MB sheet but error showing in Xwork V5.1 as "Unreliable target" 3.PXC001.D firmwared to Mbus protocol V5.10.060.Also Rx and Tx LED blinking on Controller.Data type also checked using CM2Y9774. You can see the attachments for X work programm and Mbus sheet.. Thanks, Deepak AttachmentBTU errors.docx (757 Downloads) |
1/29/2016 5:12 PM | |
Joined: 6/4/2010 Last visit: 9/30/2024 Posts: 387 Rating: (130)
|
Dear Deepak,
This is most probably an issue with the FrameTimeOut. Please try to set the FrameTimeOut (Pin FrmTio) from 500 (for 9600 bd) to 1300 (for 2400 bd). Baudrate of 2400 requires a FrameTimeOut of 1300.
Please see the attached document for further information.
I hope that this will fix your issue.
Best regards Albis AttachmentHowToSetTheFrameTimeOut.docx (734 Downloads) |