Hi, What you can try is execute a full download to OS server 2. If that does not help, you can try to delete the project on the OS server and download the project again to this server. What you can also check first is the redundancy settings on both servers in WinCC Explorer. You have to define it locally on the OS server-> Check correct network adapter etc. Make sure the redundancy settings are also set in SIMATIC Shell locally on the OS server 2. |