7/2/2013 6:11 PM | |
Joined: 2/12/2013 Last visit: 12/6/2023 Posts: 61 Rating: (15) |
hi everybody, how can i select surge suppresure for 3RH type auxiliary contactors? provide catalog if possible. |
7/2/2013 6:22 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please follow this link. |
This contribution was helpful to1 thankful Users |
7/3/2013 6:07 AM | |
Posts: 262 Rating: (45) |
Hi The link given in the above solution is the best way explained in Siemens documents that why should we use suppressors and which suppressors should be used... In addition to that i am attaching the MLFB/ Type No of Surge suppressors recommended for 3RH contactor-relay. Hope this will solve your problem AttachmentSurge_Suppressor.pdf (604 Downloads) |
7/3/2013 8:09 AM | |
Hi, Its there in the attached file.... welll see itonce again |
7/3/2013 9:10 AM | |
hi thanks for reply.i got it.. |
7/4/2013 8:50 AM | |
Posts: 202 Rating: (16) |
Hi there for 3RH Aux. contactors the rc element is same as the 3RT i.e 3RT29 16-1CD00 it could be used in 3RT contactors too.
7/4/2013 2:24 PM | |
Posts: 39 Rating: (9) |
Very good. keep it up. |