At the digital inputs of a 230 LOGO! signals with 5 VDC cannot be evaluated. The switching thresholds for recognizing a LOW or HIGH signal are higher (see appendix). And the 230 LOGO! has no analog inputs. If you want to evaluate 5 VDC with an analog input, you need the analog extension module AM2.