Hello, 3.10.1 Hardware limit switches (S7-1500, S7-1500T) https://support.industry.siemens.com/cs/ww/en/view/109781849 A reason could be, when the positive HW-limitswitch is activated by hand, when the axis moves in negative direction, to stop the axis. It is not possible to prevent such a manipulation. Retracting The position of the axis when the hardware limit switch is detected is stored internally on the CPU. The status of the reached hardware limit switch is reset only after the hardware limit switch is left and the axis is once again in the maximum traversing range. To retract the axis after it reaches the hardware limit switch and to reset the status of the hardware limit switch, follow the steps below: 1. To enable motion in the retraction direction, acknowledge the technology alarm. 2. Traverse the axis in the retraction direction until the hardware limit switch is left. The axis must then be within the maximum traversing range. If you move the axis opposite the retraction direction before the hardware limit switch is left, the monitoring will be triggered again. The following chart shows the behavior of the status word when the hardware limit switch is reached and when the axis is retracted: |
With best regards, |
|