hello experts where can i find selection chart for field contactor? |
Last edited by: ebrahimsaadati at: 02/13/2022 08:54:25 |
|
10/3/2021 12:24 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Please refer SINAMICS DCM DC converters, Operating Instructions, Firmware Version V1.5 page 728 (snap attached) |
Last edited by: Jen_Moderator at: 10/04/2021 11:48:36Optimized link. |
|
10/9/2021 7:39 AM | |
Posts: 9 Rating: (0) |
thanks for replay is this contactor for ac side of field (field supply) or dc side (side of motor)?
|
10/9/2021 7:58 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
It is at field AC supply input side. Please check designed for AC1 type. |
10/9/2021 8:01 AM | |
Posts: 9 Rating: (0) |
my mean is this contactor: what type and rate for dc side? drive is 6ra8093
|
10/9/2021 10:26 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, I guess you are trouble shooting the problem which you faced as mentioned in this Whats wrong in this circuit? topic. Please set the parameters as explained in manual for appropriate application, i.e. for direction reversal or for braking. BTW you need to use 2pole DC contactor at output & should control its operation via drive. Since you have not mentioned DC motor field current, I presume it would not be more than 32 A. (Drive rated field current capacity is 40 Amp) You can select CONTACTOR, SIZE 2, 2-POLE coil voltage is 230 V AC 50 Hz for your application. Hope this helps. |