Hi everyone, Can I connect Pt1000 temperature transmitter to 6es7 134-4GB11-0AB0 siemens analogue input module without the use of temperature controller card. Thanks. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 03/22/2022 08:27:40New subject after splitting |
|
3/23/2022 2:16 PM | |
Joined: 5/6/2010 Last visit: 9/21/2024 Posts: 1978 Rating: (276)
|
Hello, you can't use this module to connect a PT1000. You need a module e.g. (Link to the manual) SIMATIC ET 200S distributed I/O 2/4AI RTD ST analog electronic module (6ES7134-4JB51-0AB0) |