3/8/2022 6:29 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878) |
Hello VJAKKANI, It means you want to control/operate drive via CUD DI. To change p0840 value, access level is 3 i.e. set p3 in object 1 = 3 i.e. CU unit. User need to change p0840 & other parameter values which belong to drive object, so on BOP display select object 2 & then change parameter values. Hope this helps. |
This contribution was helpful to1 thankful Users |
3/18/2022 10:02 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878) |
r002 status should be o7.1 wait for power ON signal source p0840. Please check CUD1 card slot location, parameter settings. Please refer SINAMICS DCM DC converters, Operating Instructions, Firmware Version V1.5 & SINAMICS DCM, List Manual, Firmware version 1.5 (based on 5.1 SP1) manuals for more information. |
Last edited by: Jen_Moderator at: 03/18/2022 13:01:02Optimized links. |
|
4/3/2022 11:44 AM | |
Joined: 4/6/2021 Last visit: 11/2/2024 Posts: 22 Rating: (0) |
Drive is in o7.0 |
4/3/2022 12:47 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (878) |
Please refer attached sheets which will help you to set parameters to access via BOP & modify those. Attachment6RA80 BOP Access.pdf (840 Downloads) |
Follow us on