Hello, when the dynamics are not sufficient, to stop at the desired position, because the distance is too small, then it will stop in the next cycle. So you have to check the available distance, and if it is possible to stop with the dynamic settings, when you start MC_GearOut. There are functions available: LCalcMC https://support.industry.siemens.com/cs/ww/en/view/109475569 |