Please don't post twice for the same problem. You made also here a topic: Z drive -Infeed Operation Withdraw Alarm |
This contribution was helpful to1 thankful Users |
8/28/2022 3:34 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877)
|
Hello neththi, From the attached snap it looks like Z axis triggered serious fault due to which infeed enable signal is withdrawn, (but the details of Z axis fault are not displayed.) Moreover from the attached snap it mention that any one axis is not yet referenced. So please check which axis is not referenced & its co-relation with Z axis if any. Hope this helps. |
8/28/2022 3:53 AM | |
Joined: 10/12/2014 Last visit: 2/27/2024 Posts: 66 Rating: (0) |
Sorry for that . Please excuse me. |
8/28/2022 4:26 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877)
|
Hello neththi, You need to check your PLC logic for below findings. 1. Please check infeed enable logic signals & check which signal is withdrawn i.e. OFF1, OFF2 or OFF3. 2. Please check PLC logic for alarm 700728 (probably DB2.DBX199.4, here I presume DB2 is configured for fault/alarm message) This logic will help you to find out reason of ERROR FLOW METER MOTOR Y1 fault & check if it is main culprit which interlocks with Z axis & infeed withdrawn signal. Hope this helps. |