Hi Soni as it stands and as far as I know, S7-1500R/H system still only support System Redundancy S2 (i.e. single NAP in the IO Device that supports 2 AR's, see also THIS link for more on S1, S2, R1 and R2). If I understand you correctly, you are after System Redundancy R1 so you can use the redundant NAP in the ET200SP HA. If so, this will be supported one day in the future (S7-400H systems do already support it and PCS7 seems to be the target market for the ET20SP HA at the moment). In any case, I suggest you launch a support request with Siemens to have this all verified and keep us posted about the outcome. |
Cheers |
|