I'm having Same issue right now... Old screen is TP 1500 Comfort 6AV2 124-0QC02-0AX0 I upload with prosave and tried to download TP 1500 Comfort 6AV2 124-0QC02-0AX1 I see "The device configured does not match the backup" This is un acceptable in my opinion... This must not be as this... Windows platform same resolution same specs... this musn't be so difficult. How i will find 0AX0 not reachable. We can't find the machine producer to convert 0ax0 to 0ax1 in wincc... ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 12/13/2022 09:06:23New subject after splitting |
|
12/13/2022 9:18 AM | |
Joined: 5/12/2006 Last visit: 10/18/2024 Posts: 22422 Rating: (3023)
|
A "backup" of existing devices cannot be used as "Restore" on devices with new article number or vice versa (see Engineering). This applies to manual as well as automatic backup with SIMATIC HMI Memory Card. https://support.industry.siemens.com/cs/ww/en/view/109751779 |
This contribution was helpful to1 thankful Users |
1/12/2023 12:52 PM | |
Joined: 8/3/2009 Last visit: 10/18/2024 Posts: 13982 Rating: (1760)
|
Hello scekmis@Ardbeg the newer devices are V2 devices with other HW and also other Software. Have a look at : https://support.industry.siemens.com/cs/ww/en/view/109748849 Bye Murof |