Hi , If I understand correctly, you have one ES and one OS. In PCS 7, when you mentioned 'ES", by default we will know your settings already. The ES should be the station, where you should have a multiproject/User project. If you configure your project in single user project, then it will be PLC + OS together within the project. We call this project specifc structure. If you configure in multiproject that separate the AS and OS project, we call it individual project structure. If you configure Project Specific Structure, you will have your PLC and 1 x SIMATIC PC Station (Name with your target OS Host name), then you should configure "WinCC Application" in this station and configure the OS Project Editor to have SIMATIC Standard View instead of SIMATIC Server or SIMATIC Server View. Then you should configure the OS Properties in SIMATIC Manager ->Target Path -> Browse the destination of your Target OS (Create a folder in target OS D drive or C Drive, add "SIMATIC HMI" and the ES users right to access the folder) Lastly, perform an OS Download to target OS. For more information, you may download getting start or PCS 7 Engineering System in the below link. Hope this is helpful. https://support.industry.siemens.com/cs/de/en/view/109801081 |