Hello, I cant go online to my cpu226. I use the cable 6ES7901-3DB30-0XA0. But i dident found PC/PPI in the interface setting PG/PC and when i test an oder one i have the error message specified application entry not found Thank you AttachmentProblème connection S7-200.docx (508 Downloads) |
Last edited by: Jen_Moderator at: 03/09/2023 12:05:32Text formatting optimized. |
|
3/8/2023 12:22 PM | |
Joined: 7/19/2022 Last visit: 10/14/2024 Posts: 400 Rating: (63) |
Hello Greg572, If you have installed STEP 7 MicroWin V4 SP9 on a windows 7, 8 or windows 10 operating system. After you have already installed other software such as TIA Portal. it is likely that when you go to, Set PG/PC interface and want to choose the MicroWin access point you will not find it. To solve this problem try the patch I will leave for you to download for Win 7 or 8. After installation you will have the serial cable PC/PPI on the PG/PC interface and the MicroWin on the access point of the application. Run the patch as administrator. After the installation restart the PC.
AttachmentPCPPIcable.zip (559 Downloads) |