Yes it's possible. You need to set up MSTP parameters on automation station and representing higher level functions (Building, floors). Please see attached picture. PXC5 will behave lika a BACnet router. Its also posible to do engineering on datapoints via BACnet references. AttachmentMSTP.pdf (755 Downloads) |
|
Best regards, |
|
| 4/20/2023 11:44 AM | |
|
Joined: 2/13/2015 Last visit: 10/30/2025 Posts: 5 Rating:
|
Hi, With the newest abt firmware version (5.04) the problem is solved. The communication working fine. BR. Mojo SBT |