4/5/2024 12:09 PM | |
Joined: 10/11/2006 Last visit: 11/12/2024 Posts: 5938 Rating: (816)
|
Dear TommyT15629, I would recommend use first the connection makro CN011 for Modbus RTU. Afterwards change p0700 command selection from 5 to 2 (terminal as command). Then allocate the functionality to the DI (Cn002 might be a good example) Please find section 5.5 in the V20s manual https://support.industry.siemens.com/cs/ww/en/view/109824500 |
Last edited by: Jen_Moderator at: 04/08/2024 07:11:34Text formatting optimized. With best regards, |
|
Follow us on