Hi SimonT, There is a facility to allow the drive to be made operable for a period of 500 hours Change the following parameters: U977.1= 0727 U977.2 = 0101 You may need to power cycle the drive after this. After the drive is operating, I would raise a support request ticket and enquire how to proceed. https://support.industry.siemens.com/my/ww/en/requests#createRequest You will need to provide the following parameter values to the representative in order that they can provide you with a suitable pin U976.01 = ? U976.02 = ? Regards, Graeme |