(0)| 3/25/2020 5:08 PM | |
|
Posts: 3 Rating:
|
Hi. Two years have passed since you made this question. Since I am having the same problem, can you advice whether you found a solution? |
| 12/24/2021 7:16 AM | |
|
Joined: 11/1/2019 Last visit: 11/7/2024 Posts: 8 Rating:
|
Hello. I think my answer will not valuable for you, but for another who faced with this task will be. I spent 4 hours for find solution. Most valuable siemens documentation is Process control system PCS 7 High Availability Process Control Systems (page 160). My troubel was that i make wrong connection H system CPs with Plant Bus A and B. Need to connect CP1 with PlantBusA and CP2 with PlantBusB on CPU A, but on CPU B need connect CP1 with PlantBusB and CP2 with PlantBusA. (check box is grayscalled because it screenshoted at cross-project network view).
|
Last edited by: Jen_Moderator at: 12/24/2021 08:55:20Optimized link. |
|
This contribution was helpful to
|
|
| 1/31/2025 9:20 AM | |
|
Joined: 7/17/2023 Last visit: 7/14/2025 Posts: 4 Rating:
|
Very valuable answer
|
Follow us on