11/14/2009 10:17 PM | |
Joined: 5/28/2008 Last visit: 5/20/2024 Posts: 4506 Rating: (836) |
Hello ASHOK1, Put the following settings and try: P0700 = 2 P0701 = 1 (DIN 1 = ON/OFF) P0702 = 12 (DIN 2= Reverse) P0703 = 9 (DIN 3 = Fault acknolgement) P1000 = 2 In forward direction, energize DIN 1 ( terminal 5 of MM4) In reverse direction, energize DIN 1 & DIN 2 (terminals 5 & 6 of MM4) Regards |
Ayman Elotaify |
11/16/2009 11:12 AM | |
Posts: 12 Rating: (0) |
Hello Ayman, thanks for ur precious advice. but i want to know where i can use ON REVERSE/OFF1 command. |
11/16/2009 7:48 PM | |
Dear ASHOK1, As you know that any problem may have more than one solution. One of these solution as per my previous posts. Another one is to use two external contactors to reverse direction. In any case, your solution using On+Reverse/Off1 setting of one of the DIN of the drive should work. But please check that P1032 = 0 P2232 = 0 regards, |
Ayman Elotaify |
11/17/2009 5:20 AM | |
Dear Ayman, Thanks for that solution.when On reverse/Off1 command comes then P1032=1, P2232=1 so what i have to do for that. |
11/17/2009 8:17 AM | |
The default settings of P1032 = 1 & P2232 = 1. For reversing the direction of rotation, you have to make P 1032 = 0 "Reverse direction is allowed" and also P2232 =0 These setting is not applied only when the On+Reverse /Off signal is energized. It should be set as mentioned in case you want to allow to reverse the direction. Otherwise, reversing direction would be inhibitted! To tell ou the truth. I am not sure if these setting would work with terminal settings (P0700 = 2) But what I am very much sure it's working with MOP settings. This point is not very much clear in the manuals. So, to be sure you have to try. . Thus why I thought to tell you another solution in my first reply. In any case, I will be glad to here from you the result. With best regards, |
Ayman Elotaify |