(1)| 10/12/2010 10:17 AM | |
|
Posts: 42 Rating:
|
Please check the attachment for a safety program which is described here as a starting point.I tried to make Runtime group but encountered this message: "No block is available in the current block folder ,which may be used as an F program block" Thanks in advance ROCLIM AttachmentF_BLOCK.zip (336 Downloads) |
| 10/13/2010 8:04 AM | |
|
Posts: 535 Rating:
|
Dear ROCLIM, the block FB100 from your project conains a parameter in the input-section. This is not allowed for the F-PB-block. You can either remove this parameter, or create a block without parameters in the IN / OUT / INOUT-section, which calls the FB100.
Best regards, yy1 |
This contribution was helpful to
|
|