(1)| 12/3/2010 2:00 PM | |
|
Posts: 2348 Rating:
|
On changing Manual/Auto you should ensure correct setpoint transmission. What did you mean by rate limiter function? Maybe you can post your code here? |
| 12/7/2010 6:30 AM | |
|
Joined: 1/28/2009 Last visit: 12/29/2025 Posts: 6889 Rating:
|
Dear member Why not using LMNGEN_C function which is intended to reduce effect of manual-automatic switchover.Check section 2.1.13 ( LMNGEN_C: Output Continuous PID Controller) of THIS manual for more information and also attachment for a sample configuration.
hope this helps and inform if not. regards AttachmentLMN.zip (304 Downloads) |
| 12/8/2010 9:34 PM | |
|
Posts: 22 Rating:
|
Thank you all I modified the project as mentioned.report the result. |
Follow us on