Hello Kriztof; Most problems of this type on Profibus networks are related to hardware, topology and installation of cables. Basically, your first reaction should be to check that: - youareusing approved Profibus-DP cables and connectors; - you respect the maximum length (based on transmission speed) and number of nodes (max: 32) per Profibus segment; - you review all connectors to ensure that there is no mistake in the wiriung; connection of the cable shield to the connector grouning plate is essential for removing errors. - the terminating resistors (availableon the Profibus connectors) is activeon the 2 endnodes of the bus, and nowhere else. You can find much useful information from Profibus.com here: PROFIBUS Installation Guidelines PROFIBUS Technology and Application - System Description And generally documents available from: http://www.profibus.com/nc/downloads/ Also, please show us your topology, including distances between nodes and speed of the bus, so we can help determine a cause of error. Hope this helps, Daniel Chartier |
12/23/2010 11:18 PM | |
Posts: 12 Rating: (0) |
Hello Topology is very simple, one S7-315-2DP and one MM420 0.37kW with Profibus module. Right now, I just want to create a working model so my all hardware is on my desktop. I use 1 meter long Profibus cable and original Siemens connectors (with built-in terminators). Environment it's just ordinary office so without strong EMC. I don't use grounding because my electrical line system is TN-C. I'm sure that everything except MM Profibus work well because I set up similar model but instead MM inverter I used Lenze inverter. I'm attaching my project I've created just for testing purposes. I can also provide content of diagnostic buffer from my PLC and Profinbus Scope logs. AttachmentS7-mm.zip (77 Downloads) |
Follow us on