Hello All, Does someone knows if there is a limit to the *.mdf file of the OS-server in a PCS 7 project. (2G?) Is it still allowed to deletethis file and copy it back from out the \wincc\bin folder in version PCS 7 V6.1 SP1? Thanks. |
11/28/2006 12:13 PM | |
Posts: 1776 Rating: (95) |
Hi kas, maybe the following links can help http://support.automation.siemens.com/WW/view/en/24193864 see especiallystep 7 http://support.automation.siemens.com/WW/view/en/23808649 |
11/28/2006 12:35 PM | |
Joined: 9/13/2005 Last visit: 11/18/2019 Posts: 86 Rating: (10)
|
Hi KAS, regarding the copy of runtime databases please refer to (as April already mentioned): http://support.automation.siemens.com/WW/view/en/24193864 The 2GB limit is NO longer valid because since V6.X we do not use Sybase database an longer. |