While there are a number of different views on this subject, I'm with IBN-Serviceon this oneand so is EN50174 if unshielded power cables are used without partioning. EN50174is alsoused by PI (Profibus International) as a reference for their Profibus Installation Guideline (available as a free download from HERE, see table on page 18). The issue is even more improtant when safety I/O's are used. The ligth and dark period tests that is automatically done by the F-I/O cardsreacts very sentively to any interfence and it's not fun when you get called for help and have toprove to a customer that the proximity of power cables is the cause for sporadically occuring passivations of his Safety I/O's (mind you, in that particalur case he foolishly did decide touse a multi-corecable for240VAC and 24V DC F-DI's related signals which is a definet no no). |