Hello, I would like to know how to set communication from PLC. See attached: how to map this bits with a DB inside PLC and how to use it to move motor?
|
| 9/2/2011 10:21 AM | |
|
Joined: 10/11/2006 Last visit: 12/22/2025 Posts: 6062 Rating:
|
Hello, For astandard communicationbetween an S7 PLC and S110 you can use the standard functions SFC14 / 15. You have to define adata block with thelength of informations you want to send / receive. For a positioning axis ("move forward to .... and then moveback") you can use the basic positioner in the S110 (mode: traversing blocks), the telegram 110 / 111 (setup in the end of the axis configuration in starter / scout) and the FB283 (can be download here: http://support.automation.siemens.com/WW/view/de/25166781) for cyclic and acyclic communication. |
|