1/2/2007 1:56 PM | |
Posts: 5 Rating:
Hi Late, Thank You for Your interest. I have attaced a document, where I hope You can see something. I have found out at least that CPU rack is NOT earthed with it's earthing point, only through power supply. Rauno Attachment414-2DP pictures.pdf (951 Downloads) |
1/20/2007 5:50 PM | |
Posts: 5 Rating:
Thanks Late, There is at least an old version of firmware in CP443-1 (&GK7 443-1EX11-0XE0), which in now V2.3. Quite an old one! There is no routing used, at least not in the situation when the fault occurred. The chain of events was the following: - small changes to the existing FC blocks was downloaded, no problems - suddenly, when downloading again a small change (FDB programming, in function CMP>I, theconstant value in IN2 was changed to another constant) the fault occurred. I will open a service request to Siemens Finland. Here You can also find a zip file of installed software. Thanks, Rauno AttachmentInstalled software 20070120.zip (656 Downloads) |
1/21/2007 3:33 PM | |
Joined: 1/7/2006 Last visit: 11/17/2023 Posts: 2705 Rating:
Dear Rauno, You can update the CP 443-1EX11 and also update STEP7. CP 443 -1 Firmware Update V2.6 and Unrestricted Use in any Hardware Release (6GK7443-1EX10-0XE0 and 6GK7443-1EX11-0XE0) Service Pack 1 for STEP 7 V5.4 and STEP 7 Professional Edition 2006 If everything is up-to-date you might ask Siemens Finland with a Service Request what to do. |
