(0)| 11/19/2011 10:44 PM | |
|
Joined: 11/18/2009 Last visit: 12/8/2025 Posts: 263 Rating:
|
HI Medhioen, which protocol are you using? |
| 11/20/2011 3:55 PM | |
|
Joined: 10/9/2007 Last visit: 12/18/2025 Posts: 1295 Rating:
|
Hi I don't, but I know how does Mike |
|
Energy Automation products: Sicam, Siprotec, Digsi |
|
| 11/22/2011 9:58 AM | |
|
Joined: 11/18/2009 Last visit: 12/8/2025 Posts: 263 Rating:
|
Hi Medhioen, when you open Sicam PAS Operation do you have small green play in front of IED? This way you know that IED and SICAM PAS are connected. I would advise you to import SCD file from Micom directly to SICAM PAS. Import through Digsi only if you are planning to use GOOSE between Micomand SIPROTEC relays. I dont have any experiance with Micom P143 with IEC 61850. I can only give you some hints. Use this web site to check your file http://scl-validator.erlm.siemens.de/validator/upload.html Is there some place in Micom IEC61850 configuration where you need to assign clients for RCB (Report Control Blocks) or even maybe datasets to RCB? Best Regards Ensar |